Default air through elbows

We have a chart at my shop that tells how many feet different kinds of fittings are worth. It says an elbow with a square heel and throat has the same amount of air loss as an elbow w/ a radius heel and square throat.Is this true? Excuse me if my lingo is not correct.
Reply With Quote
  #2  
Old 09-09-2004, 09:08 AM
CadMan CadMan is offline
Member
 
Join Date: Sep 2004
Location: Texas
Posts: 30
Thanks: 1
Thanked 4 Times in 3 Posts
Default

I read thru the SMACNA Duct Design book and all I found was that a radius throat is about 70% better airflow than a standard 90. Couldn't find anything about the heel though. I was interested in where you got this chart and where I might get one.
Reply With Quote
  #3  
Old 09-09-2004, 02:36 PM
tazman tazman is offline
Junior Member
 
Join Date: Aug 2004
Location: The Netherlands
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Radius is always better then square, when it is about the air resistance.
We ALWAYS use elbows with a radius. Except for the inner radius, when there is too less space we use square.

I have a simple mind and see it simple. Air likes a quiet easy ride, and not a ductsystem like rollercoaster!
Also watch out for noises!!! I never here about sound in here. There are some golden rules.
One of them is sharp edges, they can cause some noise.
Reply With Quote
  #4  
Old 10-20-2004, 02:52 PM
bordontn bordontn is offline
Professional Member
 
Join Date: Sep 2003
Location: McEwen, TN.
Posts: 212
Thanks: 0
Thanked 2 Times in 1 Post
Default

Be careful of those square throats on a radius elbow....I'm posting part of a chart which shows the resistance in feet of duct..
the itinerant tinker a.k.a. bordontn
Attached Thumbnails
elbows.jpg  
Reply With Quote
  #5  
Old 10-27-2004, 05:26 PM
Gate Gate is offline
Member
 
Join Date: May 2004
Location: Ohio, USA
Posts: 51
Thanks: 0
Thanked 1 Time in 1 Post
Default

A vaned square throat/heel ell is better for airflow than a radius heel with square throat. If you vane this configuration you need to run full vanes evenly spaced...

peace,
- Gate
Reply With Quote
  #6  
Old 03-05-2008, 09:25 AM
energystar energystar is offline
Junior Member
 
Join Date: Mar 2008
Posts: 5
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I was told by an engineer that a radius throat with a square heal is the way to go. It's better than a sq/sq with no vanes
Reply With Quote
  #7  
Old 03-05-2008, 03:36 PM
Bud's Avatar
Bud Bud is offline
ME
 
Join Date: May 2003
Location: Waukesha
Posts: 2,101
Thanks: 415
Thanked 125 Times in 88 Posts
Default

Better then vanes? I don't think so. The radius throat and heel is great way to fab elbows, and you really want to learn more about the radius to width ratio for maximum air flow or air flow with the least resistance. If you can't use a radius throat, you should probably consider vanes to help the air flow around the corner.
Reply With Quote
  #8  
Old 03-05-2008, 07:53 PM
legacy legacy is offline
Member
 
Join Date: Oct 2006
Posts: 62
Thanks: 1
Thanked 1 Time in 1 Post
Default

We once had a guest speak at a union/management committee day, he was representative from the ITI (body that governs all SMWIA apprenticeship programs). ...Anyway, he was retiring from the ITI and was moving from CA to TN and was having a house built. On one of his final trips to check on construction, he noticed that the HVAC constractor had used all srare throat/ radius heel 90's. He made the take them out and replace them with full (1-1/2X) radius 90's where they would fit and sqaur with vanes where they did not.

I have made sq throat/radius heel for people that have walked into my shop looking for duct, but have never made that fitting for one of my jobs.

Just like a point to point (no miter) offset, if you measure the distance from the inside of a square throat to the mid point of the radius heel of a sq/rad 90, its got to choked down by at leats 10%-15% I would think.
Reply With Quote
  #9  
Old 10-21-2008, 03:50 PM
cactassdupree cactassdupree is offline
Professional Member
 
Join Date: Aug 2008
Location: Sunny Florida
Posts: 602
Thanks: 161
Thanked 58 Times in 49 Posts
Default

Antone heard of double Vanes? they are 2 pcs. per vane
Reply With Quote
  #10  
Old 10-21-2008, 06:23 PM
device device is offline
Professional Member
 
Join Date: Feb 2007
Location: Left Coast Canada
Posts: 620
Thanks: 190
Thanked 93 Times in 74 Posts
Default

the aerofoil type..
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


 

All times are GMT -6. The time now is 06:33 PM.


Powered by vBulletin®
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.